Did I do an okay job on this install?

inforlonghaul

Getting the hang of it
Joined
Jul 12, 2015
Messages
61
Reaction score
26
This is an internal project and I'm certainly no professional, but I thought I'd put these few pics on here for critique. I feel like I did a decent job looking at some of the examples on here and many of the "what not to do" forum posts, but I know there's always room for improvement. Whats your thoughts on this? Is there anything I need to do to help secure the conduit fittings from rain? I did use the outdoor rated junction boxes. I still need to put a few more conduit straps on to ensure it's all good and secure. I took these at the end of the day and needed to get home.
 

Attachments

TonyR

IPCT Contributor
Joined
Jul 15, 2014
Messages
17,651
Reaction score
41,095
Location
Alabama
Looks nice, about the only thing I can mention is "next time" consider using compression EMT fittings (couplings, connectors at box and at elbow) instead of set screw version; the set screw type is more prone to water incursion.

After you put up those additional clamps/straps you mentioned, if you have a good, long hot spell you might see a little expansion from the heat on that many pieces of conduit, maybe not. If you do, just loosen the set screws of a coupling or 2 or a one or 2 connectors and allow the conduit expand into it then tighten them while still warm. It's only a slight chance, there may already be room for it to move and you'll never notice. It's usually VERY long runs on a west wall that are affected the most.

Great job! :cool:
 