Yep, Bubba's been in the breaker panel again...:facepalm: :lmao:
I'll add my own project to this thread.

Didn't realize the panel only allowed tandems on the lower 5 slots when I tore into it.

I did however get around to replacing the 4 circuit 20A quad breaker with proper 15A ones. Apparently my solar installer didn't have 15A tandems when he needed to make room in the panel, so I got a used 20A that must have been banging around in the back of his truck (switch partially broken).

Now I'm annoyed he put that 35A solar breaker in the last 2 slots I can fit tandems. I'm wiring in an EVSE and need to free up 1 more slot.

 

TonyR

IPCT Contributor
Joined
Jul 15, 2014
Messages
16,771
Reaction score
39,033
Location
Alabama
So there are conductors with white insulation that are hot, like the 2 pole "Solar" breaker at bottom right?
Or am I not seeing it right? :idk:
 

redpoint5

Getting comfortable
Joined
May 12, 2020
Messages
496
Reaction score
1,558
Location
PDX
So there are conductors with white insulation that are hot, like the 2 pole "Solar" breaker at bottom right?
Or am I not seeing it right? :idk:
It's the weird perspective. It has a red and a black going to it.
 
Joined
Aug 19, 2020
Messages
4,936
Reaction score
20,748
Location
San Antonio, TX
I'll add my own project to this thread.

Didn't realize the panel only allowed tandems on the lower 5 slots when I tore into it.

I did however get around to replacing the 4 circuit 20A quad breaker with proper 15A ones. Apparently my solar installer didn't have 15A tandems when he needed to make room in the panel, so I got a used 20A that must have been banging around in the back of his truck (switch partially broken).

Now I'm annoyed he put that 35A solar breaker in the last 2 slots I can fit tandems. I'm wiring in an EVSE and need to free up 1 more slot.

WAY out of my league......wow.
 

TonyR

IPCT Contributor
Joined
Jul 15, 2014
Messages
16,771
Reaction score
39,033
Location
Alabama
Don't know why but it bugs the crap out of me to hear actual (so-called) 'electricians' call a female wall receptacle a "plug"....... a plug is a male device, a receptacle is female. Heck, even calling it an "outlet" or "socket" wouldn't bother me. Some of the circuit breakers in the image triggered me, the dude that wired my house did the same thing on my panel.

Even NEMA labels the typical 15 amp female outlet as "5-15R" (R for Receptacle) and the male plug "5-15P" (P for Plug).

Yeah, I know.....the wife says I'm anal. But I dealt with those devices and names for 40 years and long before we were married, so....:cool:
 
Last edited:

redpoint5

Getting comfortable
Joined
May 12, 2020
Messages
496
Reaction score
1,558
Location
PDX
Well I'm doing everything wrong it seems.

  • 6awg NM-B is the wrong wire because it has a 60 degree C rating, which de-rates it to 55 amps, which is less than the 60A breaker I need to run the 48A continuous circuit (the 80% rule).
  • The bus will have a rating of either 200A or 225A for my 200 amp service. It's not permissible to add another source of power (my solar array) that when combined with the main breaker rating exceeds the bus rating. I'm at 135A.
    • The exception to that rule is to place the solar breaker at the opposite end of the bus as the main breaker, which is what the solar installer did. I can't move that breaker.
  • Tony pointed out I mislabeled breakers with 'plug' :facepalm:
I'm sure my plan would also include other violations I'm unaware of.

I should have gone with my initial instinct to remove the dryer circuit and just use that spot.

WAY out of my league......wow.
Out of my league too, as I'm discovering.

Don't know why but it bugs the crap out of me to hear actual (so-called) 'electricians' call a female wall receptacle a "plug"....... a plug is a male device, a receptacle is female. Heck, even calling it an "outlet" or "socket" wouldn't bother me. Some of the circuit breakers in the image triggered me, the dude that wired my house did the same thing on my panel.

Even NEMA labels the typical 15 amp female outlet as "5-15R" (R for Receptacle) and the male plug "5-15P" (P for Plug).
I used plug just because it's shorter than spelling receptacle, which wouldn't fit on the breaker... but I should have just used 'R' to designate receptacle, and maybe 'L' for lights. It got pretty confusing with Master bath lights, fans and receptacles on the same circuit as master bed lights and receptacles. The receptacles in the bath had a dedicated circuit... so I couldn't just label a circuit as Master Bath, or Master Bed since they share circuits. Lots of that room sharing going on making labeling not so straight forward.

I wrote it all down in detail in a notebook, trying to figure out how this house is wired. I still have 2 switches I have no idea what they control.
 
Last edited:

TonyR

IPCT Contributor
Joined
Jul 15, 2014
Messages
16,771
Reaction score
39,033
Location
Alabama
I used plug just because it's shorter than spelling receptacle, which wouldn't fit on the breaker... but I should have just used 'R' to designate receptacle, and maybe 'L' for lights.
Hey,man...I didn't mean to sound like I was getting onto you, I don't have that right and it's not really my style...besides you didn't ask for my opinion. :cool:

I think you're doing pretty damn good, BTW.
 

redpoint5

Getting comfortable
Joined
May 12, 2020
Messages
496
Reaction score
1,558
Location
PDX
^ WTF? How does that even occur to someone? :idk: :wtf:
When there's an extended power outage, and you realize you can cut the socket end off an old extension cord and put another plug on it so you can hook your generator into an outlet of your choosing to energize the whole circuit. I would never...

Instead I wired the cut end directly into the breaker panel for the week we were without power.

Anyhow, powering the outlet with an energized plug reminded me of that very not recommended hack.
 
Last edited:

Mike A.

Known around here
Joined
May 6, 2017
Messages
3,831
Reaction score
6,389
When there's an extended power outage, and you realize you can cut the socket end off an old extension cord and put another plug on it so you can plug your generator into an outlet of your choosing to energize the whole circuit. I would never, though...
That I can understand. But doesn't look like what happened here. They put some work into it and looks good all the way up to that point.
 

redpoint5

Getting comfortable
Joined
May 12, 2020
Messages
496
Reaction score
1,558
Location
PDX
That I can understand. But doesn't look like what happened here. They put some work into it and looks good all the way up to that point.
I'd have gone with speaker wire with 2 blade terminals on the ends shoved into the socket instead of putting all the effort into that nonsense. If laziness is called for, go full lazy.
 