So now your neighbor has some issues less than 2 weeks after you?
Have you read your 120/240 to see if one or both legs are not too high?
I replaced the dryer heating element in a 4 year old Maytag dryer last summer. Leading up to that it kept shutting down with a displayed error code "AF" (Air Flow). No blockages found, no lint buildup anywhere but ran a brush snake anyway all thru the 10 ft. of galvanized vent pipe, blew it out with a gas lawn blower and insured the flexible hose was not foil but metal and was clean.
After another 2 weeks of "AF" (no, not me saying "Aw, F*ck!"), my APC UPS on the TV which has the high limit for detection jacked up to 135VAC because of the 3.5kW portable generator's antics it started beeping and read 138VAC on it's LCD display. I pulled the main panel's surround and measured 140VAC each leg, 280VAC across both legs for the @#$% 240!
No wonder the dryer heater element burned up and was running hot...it's meant for 240, not 280!
I called the local co-op utility, guy came out, looked at me when I told him and he's thinking "yeah, this old fart's crazy...probably has a bird nest in the dryer vent and measured the voltage with a $8 Harbor Freight meter". He went up in the bucket and came down 15 minutes later, wouldn't make eye contact and said a sheepish "Yeah, lightning must have got it, the primary voltage is correct, no one else nearby has a problem, you're the only one on this transformer and your 240 DOES read 280 so I'll change out your transformer."
He did and there's been no more problems with "AF" since summer of 2024. If you haven't done so, I'd check it.....got nothing to lose!