Again, it's most likely a problem with the wiring in the building. Different ground potential differences will cause some horrendous damage. Is there any electric motors that start/stop, especially larger ones with capacitive start, in the building? Are there any sources of high power radio frequencies nearby, a radio station or ham operator?

I still suspect poor grounding and poor bonding of the electrical system and all the metal of the building. I know I'd be wearing rubber gloves working in there just to avoid getting nailed myself until it is traced and properly repaired.
 

oh6hfx

Getting the hang of it
Joined
Jun 26, 2016
Messages
120
Reaction score
38
Location
Lohtaja, Finland
Again, it's most likely a problem with the wiring in the building. Different ground potential differences will cause some horrendous damage. Is there any electric motors that start/stop, especially larger ones with capacitive start, in the building? Are there any sources of high power radio frequencies nearby, a radio station or ham operator?

I still suspect poor grounding and poor bonding of the electrical system and all the metal of the building. I know I'd be wearing rubber gloves working in there just to avoid getting nailed myself until it is traced and properly repaired.
I was asking them the same about big motors or big power devices, but there is none in use anymore in the farm. Also no big radio tx nearby that I know.

We'll see later what they found. It has to be something to do with power outages.
 

Teken

Known around here
Joined
Aug 11, 2020
Messages
1,616
Reaction score
2,921
Location
Canada
Just some clarification on terminology for those who may stumble upon this topic in the future. I know people often generalize because its the first thing that comes to mind but in this case its important to call out the distinctions. ESD (Electro Static Discharge) is normally associated with a person who builds up a positive charge and then relays the same to an object upon being touched.

Think door knob . . .

ESD is a huge problem when repairing any sensitive electronics and hence why ESD mats, wrist bands, and equipment is properly grounded.

ESD is not the problem here as it is more likely a surge event whether it be from interior generated (micro surges) or more likely external in nature. As others noted any time there is a voltage difference (potential) in ground reference anything can happen.

Keep in mind what I stressed about slow creeping voltage whether it be rise vs sag.

If there is something wrong with the incoming power supply to the home such as a creeping voltage rise (above 130 VAC) this condition will release the magic smoke out of the box. Again, an extended voltage sag (brown out) below 90 VAC will also cause things to go poof!

Why???

Because lots of electronics now use buck / boost electronics to maintain a steady flow of power to the appliance. This loosely speaking (buffered) power allows a device to ride out variations of voltage swings without issue. One only needs to look at the specifications of any security camera whether its for POE vs 12 VDC. The spec literally says X system will operate from 38 - 5X volts POE vs 12 VDC is 25% swing either way!

That's literally 9 volts ~ 15 volts on a 12 VDC system . . .

That is awesome in terms of operating voltage and allows that device to run fine in varied electrical conditions. But this loose range injects something that many people fail to understand when ever I note about:

When voltage drops current rises . . .

This statement always confuses people because their only reference is basic Ohms law and that only applies to simple resistive circuits. Because in those simple resistive circuits that doesn't happen. When voltage drops so does current and matches in lock step. In a complex highly regulated PSU like a camera the system is designed to accept a INPUT power of varied voltages. But at all times has a highly regulated 3.3, 5.0, 12 VDC rails kept at constant states to insure high reliability and operations.

Hence when voltage sags (brown out) that highly regulated PSU will continue to draw more current to satisfy its operations but in doing so it will burn out whatever.

The above scenario always explains why if a system that incorporates power protection like HRC fuses, MOV, PTC, Zener, etc why they never blow. Again, all of the above are designed to react to sudden quick surges but are not designed for slow rise (creeping voltage) whether it be AC vs DC. As the OP showed there were PTC's and possible MOV's in one photo that didn't break open from a visual perspective.

Regardless, in the ideal world everything should be at the same potential and referenced to a single point (Earth) ground from the incoming utility. As noted in the past one problem I've seen in commercial installs like the OP is where the building uses some kind of metal cladding which isn't at the same ground potential. In those cases it caused anything from a ground loop and you would see lines on the video to popping noises in the audio.

The easiest thing to do as counter to what many would think to do is to Decouple the camera from the metal frame. This is normally done by using a plastic junction box that also uses a foam insulator. Now, the camera uses just the ground coming from the power wire whether it be from POE / 12 VDC. :thumb:

None of this is rocket science but does take some common sense to understand, identify, and implement when needed.

As noted early on before the POCO comes on site you can double check all of the wires going to any breaker is tight. Verify all ground and neutral bars are corrosion free and also tight in the service panel. Go to main water main and if your location bonds to the incoming water source that this bond is secure and corrosion free. Move inspect all outlets and switches in the home and confirm all wiring is tight and secure to their respective point of use.

This is also a good time to walk around and inspect every piece of electronics in the home. Besides the obvious visual inspection take any small electronics and pick it up and smell it. Do a rattle test and if you hear things bouncing around its going to be a piece of electronic component that literally just blew up! :facepalm:

Why is doing this basic step important???

Because these same electronics are literally a fire hazard waiting to explode and light on fire. They also are a direct point of micro surges and noise related issues from RFI / EFI. In North America all new houses incorporate AFCI (Arc Fault Circuit Interrupters). Their only goal in life is to detect micro arcs happening in the walls in the buildings envelope.

This is what's happening when you don't check every piece of electronics after a huge lightning strike that was proven to damage one major appliance. If it took out a random piece of appliance like a stove, fridge, microwave, dishwasher, washer, dryer. What are the odds it didn't impact a cheap radio, TV, boom box, name anything that's electronic in nature!

Nine times out of ten you will quickly find visually or through smell something else was damaged from that first strike. Those who live in Lightning Alley know this information to be true and expect to find something dead or damaged.

As an aside I've been heavily involved in energy management & energy control for more than 30 years. In a past life this was major part of my profession and now is a big hobby in my personal life. I have many power quality monitors and energy management systems that track and monitor every aspect of my homes incoming power. Below is a very old image capture that shows one of the systems being fine tuned and calibrated to the Nth degree.

The system isn't normally set to capture Normal line voltage conditions but I wanted to see what the system would capture while my back up power systems were being deployed. As seen here the system captured voltage sags, frequency drifts, voltage rises, and the duration of each. Having such tools in place allows factual information to be obtained and relayed to the POCO if and when required. There's no guessing, there's no I dunno, there's only the material data to provide and for them to resolve! :thumb:

 

Dingoboy

n3wb
Joined
Oct 15, 2020
Messages
24
Reaction score
9
Location
Saint Cloud, Minnesota
I have installed cameras on a site 4 years ago. There has been several devices damaged during these years. Poe switches, cameras, wifi access points and injectors.
There are cameras in 3 buildings, and internet / lan connection to NVR is done with 2.4GHz wifi outdoor TP-link access points. In all other buildings everything has been working fine since installed, but one, a barn for sheeps is a problem place.

First I thought it was the thunder which was killing the devices, then I thought it is some kind of inducted ESD in outdoor access point. Two weeks ago, there was again something
gone broken, and I found it is the poe switch and camera. As here we don't have thunder this late of year, I just thought, well the switch was bad quality and I replace it with poe injector and put a new camera.
It worked well for 2 days and then it happened again. There had been just a normal power outage in power network, and this time everything in the camera system was damaged.
48V poe injector for camera, Dahua camera itself, 24V injector for wifi access point, and wifi access point of course.

I decided to replace the U/UTP cables with F/UTP and put an extra surge protector for access point, grounding that to buildings yellow-green safety ground. So far it has been working fine.

Later I opened the damaged devices. Injectors and camera are burnt bad! In access point I can not see any damage or black components, it even works with poe, just the lan connection does not work anymore.

The question is: where is the surge coming? Is it a voltage spike from AC network hitting the injectors and going via ethernet cables to other devices burning them also? In this one picture you can see cameras poe injector and it is burnt
from the side where LAN connectors are. It's just the same with wifi poe injector. In wifi poe injector even solder has been melted in LAN connector and I could pull it out with my fingers. In both devices the most bad place is around LAN connector, not poe connector.
Does the farm owner use an electric fence for his/her livestock? Having been born and raised on a dairy farm in the upper mid-west, I have seen many instances of incorrectly grounded fences cause issues such as electrifying water supplies, building walls (typically steel walls), etc. I didn't see any mention of your client having one, but the fence is the very first thing that came to my mind.
 

oh6hfx

Getting the hang of it
Joined
Jun 26, 2016
Messages
120
Reaction score
38
Location
Lohtaja, Finland
Does the farm owner use an electric fence for his/her livestock? Having been born and raised on a dairy farm in the upper mid-west, I have seen many instances of incorrectly grounded fences cause issues such as electrifying water supplies, building walls (typically steel walls), etc. I didn't see any mention of your client having one, but the fence is the very first thing that came to my mind.
I am not sure about that. Sheeps are not outside this time of year anymore, but it is possible it was in use when the last damage happened... have to ask.
 

garycrist

Known around here
Joined
Sep 25, 2021
Messages
2,367
Reaction score
6,967
Location
Texas
I do not believe the electric fence is the culprit. If enough current went through the fence,
to smoke components, as shown in the pics, it would be lethal to animals.

I believe you must find the high current source, not a high voltage source.
 