I used a tracer/tone and found out i had an extra pair of wires from keybus to panel so. I purchased a PC5801 expander now i have another issue.
This is what I'm working with; PTK5507, PC1616, PC5801
My issue is zone 9 works as expected, the rest of the zones 10 through 14 do not (15, 16 are null)
I have verified jumpers for PC5108 are correctly installed, I have done a proper enrollment with section 902, followed by a 1-minute wait, then verifying that Zones 9-16 appear in section 903. I have also verified that section 203 shows ON for 123456 (7 and 8 are null) I have assigned Zone types under 001 (1-14 ) 9 thru 14 are 03
Zones 1 through 8 with PC1616 have EOL resistors and work as expected, the PC5108 zone 9 works it to has EOL resistors, 10 through 14 are window contacts they do not have EOL resistors. I have also run a continuity check on zone 10 thru 14 ( window contacts) and they respond as expected. Zone 10,11,12,13 are always open, and 14 is closed no matter what I do I cannot change zone 10 thru 14.
I created a test line at the panel (door contact with EOLR) tried Zone 10 through 14 the results were the same
I'm thinking I've either missed a programming step (even though zone 9 works) or my expander has issues
Did I miss a step? or have bad zone expander?