Finally got power back today at 4:30pm. They replaced a very large transformer in a neighbor's back yard.
So,
@IReallyLikePizza2 if you could elaborate/comment for me on these points below, I would really appreciate it as I am going to pull the trigger on a gen for the house.
From your posts I gather the following:
- Liquid cooled are quieter than air cooled
- The 1800 rpm models are quieter than the 3600 rpm models
- Liquid cooled models have a longer time between oil changes than the air cooled models?
You state that you would now buy the Kohler RCLA30. Why?
I have been looking at spec pages and the Kohler page states the RCLA30 is for 125amp service. They recommend the RCLC48 for a 200amp service. We have a two-story home of 4100sqft, 200amp service, and two AC units. What is your take on the sizing?
How do the Generac and Kohler compare for reliability and serviceability? I see some literature stating to check the oil every 8-12 hours. Some say every 24 hours.
Liquid cooled 1800RPM = Best
Liquid Cooled 3600PM = Better
Air Cooled 3600 = Good
Air cooled is less complex, but is of course cooled by air. Here, the air is hot as shit. Make of that what you will! The liquid cooled models also usually have higher ambient operating temps before being derated
Liquid cooled models do NOT have a longer time between oil changes, interestingly. For example, my genset wants an oil change every 125 hours, but the air cooled Generac wants one every 200 hours. I suspect Generac are quoting these times based on the target audience for the generator, and a calculated lifespan of the engine.
Tell me how a larger engine running at HALF the RPM, and liquid cooled, needs its oil changed sooner? Makes zero sense. I worry about the air cooled units with 200 hour oil changes. I would change mine at 100 if I had an air cooled.
I would go with the Kohler RCLA30 as Kohler is an objectively better brand than Generac. Generac and Cummins are no longer able to source the 2.4L engine they used in their liquid cooled gensets around that size. So now if you want an 1800RPM liquid cooled genset from Generac, you have to go all the way up to the 32kw XC series. Thats a 4.9L engine, very overkill. The Kohler RCLA30 is the perfect sweet spot for a house IMO
Kohler is a better brand 100%, no one will argue that. However, Generac have the numbers on their side. For every Kohler genset there is probably 10 Generacs, which means they see the problems and fix them sooner. I've heard of plenty of people with issues with Kohler Gensets that they had a hard time getting fixed. Generac's may have their problem, but there is SO MANY of them out there. Its like the Ford of generators.
A big plus of Generac is extensive Genmon support, which I love.
I would not check the oil every 8, 12 or 24 hours honestly. Who wants to shut down their genset? Not me. They all have low oil shutoff and low oil pressure shutoff. Make sure its full and change the oil at the interval required. If I had an air cooled genset, maybe check at 100 hours, if you can.
It will shutoff before it damages the engine either way